a shopping mall had a flush mounted panel on the 12' ceiling of the walkway around the mall, it was probably for the high hat lights that illuminated the covered sidewalk (one of those outside malls). legal/illegal?
 
Are you saying that the panel is mounted 12' about the ground?

If so 240.24(A) requires that overcurrent devices be mounted so the operationg handles are not more than 6'7" above the floor or working platform.