minnesota. inspector says panels have to be clearly marked on the exterior as to voltage. What code requirement is this???
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: panel labelling

He's stretching it just a hair, but he is close. look at 408.13 this will send you to 110.21.

Opening a cover or door is not the same as needing to go inside the panel for the labeling, so if the label is located behind the door all is fine.

Roger

[ September 11, 2003, 10:15 AM: Message edited by: roger ]
 

hbendillo

Senior Member
Location
South carolina
Re: panel labelling

Did you ask if there is a local code requirement for this? The NEC does not mandate this from my interpretation. However, it is a good idea.
 