I'm designing as beginner using a 120/208V panel schedule that shows the following loading:
Phase A: 439,304VA, Phase B: 364,136VA, Phase C: 370,820VA
Total: 1,174,260VA
So if I look at the total VA of 1,174,260VA does this mean that the panel has a load of 1,174,260/208/1.73 = 3,259A? I would then use this number as the load, and the minimum that the main breaker could be 1.25(Safety factor) x 3,259A = 4,074A? So, main breaker size would be AT=4200A, AF=4200 and AIC=5000. Is that correct?
Can anyone provide the good example AT/AF/AIC specification such as manufacturer? As each phase load do not draw evenly in the three phase system , in case, calculating the largest phase load to select 3P breaker size or wire size. Am I right?
Also, is there such a breaker size of 4,000A as a low voltage?
When calculating of wire size for this phase A load, 4,074A /10=407 A, then ten set of 600 kcmil was available for this phase leg.
I just wonder if this calculation is correct or realistic !! Otherwise, I highly appreciate if you provide your ideas to me.
Thanks
Phase A: 439,304VA, Phase B: 364,136VA, Phase C: 370,820VA
Total: 1,174,260VA
So if I look at the total VA of 1,174,260VA does this mean that the panel has a load of 1,174,260/208/1.73 = 3,259A? I would then use this number as the load, and the minimum that the main breaker could be 1.25(Safety factor) x 3,259A = 4,074A? So, main breaker size would be AT=4200A, AF=4200 and AIC=5000. Is that correct?
Can anyone provide the good example AT/AF/AIC specification such as manufacturer? As each phase load do not draw evenly in the three phase system , in case, calculating the largest phase load to select 3P breaker size or wire size. Am I right?
Also, is there such a breaker size of 4,000A as a low voltage?
When calculating of wire size for this phase A load, 4,074A /10=407 A, then ten set of 600 kcmil was available for this phase leg.
I just wonder if this calculation is correct or realistic !! Otherwise, I highly appreciate if you provide your ideas to me.
Thanks