I have a three phase motor/pump, 3 phase 208 volt rated at 2 HP. Im trying to determine panel loading for both continuous and non-continuous loading for purposes of balancing the loads on the phases in the panel. (kva on all the phases)
Ive been through ch 4 but cant find the answer. Can someone point me to the correct section in the NEC?
My interpretation for the continuous loading was to take
2hp* 745.6 = 1491 watts -> 1491/208 = 7.17 amps. using the value from table 430.250 i get FLC of 7.5 amps.
this gives me 1.56 kVA/phase; is this correct? what if this was a intermittent duty motor?
thanks