Hey guys...I'm also a Noob and loooking for some help.
I'm working on a project where we are installing a new 60A branch circuit in an existing panelboard and the jurisdiction wants us to verify the existing feeders are adequate for our loading. Our actual new design load is in the 7.24 KVA range.
The panel board is 225A with #2 wires feeding it. It is 120/208V, 3phase, 4W. The C/B's are as follows:
(11) 20A, 1p, receptacle breakers
(1) 30A, 3p, heater (for pool) breaker
(4) 30A, 1p dedicated receptacle for treadmills breakers
Is there a quick way for me to estimate loading? The examiner tried to tell me us 80% of the breaker size...does that seem right? Can I estimate a 20A, 1p at 1.92 KVA (20A * 80% * 120)? How do I deal with the three phase load estimate?
I'm guessing using this conservative estimation will cause us to have to upgrade wire size, but without tracing all 16 circuits, how else can this be approached?
Any help appreciated!
I'm working on a project where we are installing a new 60A branch circuit in an existing panelboard and the jurisdiction wants us to verify the existing feeders are adequate for our loading. Our actual new design load is in the 7.24 KVA range.
The panel board is 225A with #2 wires feeding it. It is 120/208V, 3phase, 4W. The C/B's are as follows:
(11) 20A, 1p, receptacle breakers
(1) 30A, 3p, heater (for pool) breaker
(4) 30A, 1p dedicated receptacle for treadmills breakers
Is there a quick way for me to estimate loading? The examiner tried to tell me us 80% of the breaker size...does that seem right? Can I estimate a 20A, 1p at 1.92 KVA (20A * 80% * 120)? How do I deal with the three phase load estimate?
I'm guessing using this conservative estimation will cause us to have to upgrade wire size, but without tracing all 16 circuits, how else can this be approached?
Any help appreciated!