Re: Panel located near geothermal lines
The rule prohibiting water lines underneath a panelboard is either wise or utterly cretinous depneding on the situation. If there is no pipe joint underneath the panel and there is not a way to use more than say 3 bottom knockouts such as in a basement then this part of the rule is utterly cretinous. Same goes for a relocated panel in a slab on grade building and it is wholly rediculous to run new conduits underneath the slab.
I know someone who has a slab on grade commercial building where there are zero conduits going directly from a panel to underneath the slab. The only circuits underneath the slab are for the well pump and a post light. A replacement panel is over a 1" copper water pipe and both elbows at the room corners are 2 feet away. In order to move the pipe the pipe would actually have to go across the ceiling which would increase the hazard from leaks or condensation. This room is not air conditioned during the summer which means that a pipe across the ceiling will drop condensation all over stuff. This panel is in the same room as the pressure tank and switch for the well and the boiler for the forced hot water heat. Only 1 bottom knockout is used which is 1/2 EMT to supply the pressure switch for the well pump.
If a pipe decides to split or otherwise fail water will be all over the place. An inspector tried to say that this small room had to have a sprinkler head in the ceiling but the vice chief inspector dropped the issue while his boss was on vacation. A year later this snotty chief inspector retired. Turns out that there was no requirement in Ohio Building Code for a sprinkler head in this type of building because the walls were concrete block.
[ May 19, 2005, 03:29 AM: Message edited by: mc5w ]