Re: Panel Location to Transformer
Originally posted by charlie b:
Quite true, Bob. That word "likely" is key to the requirement. But I would wager that there isn't an AHJ in the country (OK, that there are not more than 3) who would accept the notion that a panelboard (or "load center," to use the phrase from this question) is unlikely to require maintenance while energized.
I would say it would depend on the loads served. If there are no loads that would be missed for the duration of the maintenance task, then I would say you can crowd a panel.
If it were the primary panel for a dwelling, I'd say it's highly unlikely that the panel will be de-energized for service.
I have a house panel on a sixplex that I have no room for, and install above the main disconnect. Technically, I am in violation of 110.26(A)(3), because the main disconnect sticks off the wall by 18", and I am only allowed 6". My argument was that there were no loads present that couldn't be shut off. It has:
* 1 120V 15A circuit for the fire-room GFI and keyless
* 1 240V 15A baseboard heater in that room,
* 1 240V 60A feeder for a detached garage, which supplies pole lights
* 1 120V 15A dedicated circuit for the horn strobe, which consists only of the 120V strobe switched by the flow. The LV fire alarm is on the other side of the flow, and is still operational when the flow closes contacts. Monitoring is not interrupted. In the unlikely event that a fire starts during the period of maintenance, the fire department will still be dispatched.
I would feel totally comfortable shutting down my house panel for maintenance. One factor I hadn't thought of: I should probably put a label on the panel to state it has no crucial loads, and can be momentarily disconnected for maintenance. Just because I know, doesn't mean the next guy will.
Besides, it's nice having the disconnect under it - it makes a good shelf for tools.
The AHJ was compassionate about the total lack of space I was given for the service, the phone and TV demarcs, and house panel. I gave up my prime panel location to ease the burden on the LV guys - there was literally no space for their undergrounds to emerge into a box on the wall, if I didn't move.
Commence with the rock throwing.