panel mounted power quality meters?

Status
Not open for further replies.

Huntxtrm

Senior Member
Location
Cleburne
We are having issues at our plant with power quality and power balance. Old plant, old equipmentioned in place. lots of motors. power company makes us black out from time to time, because of power quality problems. any recommendations on power quality Meters? panel mounted at the distribution panel. we have old analog a meters with donuts in place at the moment. The don't work. any info on testing those would be appreciated also. Thanks Boys.
 
We used Dranetz and Fluke for their portable power quality meters. For permanently mounted, we use Schneider & Siemens.

You will need new CTs as the old ones will likely not be sensitive / responsive enough to pickup power quality issues. Avoid split core CTs for PQ metering, since they are less accurate.
 