dwcook50

New member
I am designing a control panel for a client that has grown into a 70A demand for the 24VDC. Is there a code issue having three 20A and one 10A hooked in parallel?
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: PANEL MOUNTED POWER SUPPLIES!

It sounds like you want to put 3 power supplies in parallel. Is this correct? It is generally a bad idea to put power supplies in parallel unless they are specifically designed for that use. The reason is that if one produces a slightly different voltage, a large current will flow from one supply through the other supply. The results could be very bad to say the least.

The only code reference I can think of off hand that might apply would be the requirement to install equipment per the manufacturer's instructions. Unless they say you can parallel their power supplies, I wouldn't suggest it.

Steve

PS. Power supplies designed to be placed in parallel would have some type of feedback to track the voltage of the other supply and keep the difference to a very small amount.
 

pwhite

Senior Member
Re: PANEL MOUNTED POWER SUPPLIES!

there is a company that makes a 100,125,... up to 250 amp power supplies. the 125 amp unit if memory serves me correctly is $ 1,600 each 12 wk delivery. e-mail me and i will forware the information to you. i am on vacation this week & just happened to be at a computer.
 