Panel NEMA rating in commercial bathroom

Status
Not open for further replies.
Are you installing it in a place that water splashing would be a common occurance during use? and -- outside the scope of 240.21?
 
Is a NEMA 1 rating for a recessed panelboard in a commercial bathroom ok?
Is it the Main Service Disconnection means..if so NO per 230.70(A)(2)...or if it is a Remote Distribution Panel in a commercial bathroom then YES...it would be fine as long as it is not installed in a location what someone would argue is a wet or damp location...and just in a bathroom, in general is not either of those types of locations.
 
I had a bad experience, the NEMA 1 switchboard is supplied without door and breakers not sealed, it's not suitable at all for dusty areas.
 
Is it the Main Service Disconnection means..if so NO per 230.70(A)(2)...or if it is a Remote Distribution Panel in a commercial bathroom then YES...it would be fine as long as it is not installed in a location what someone would argue is a wet or damp location...and just in a bathroom, in general is not either of those types of locations.

Thank you, not a main service disconnecting means.
 