A home owner was required to get his electrical panels inspected prior to them doing a inspection. He has one 100A fuse box in a closet that you need to be a contortionist to get at. It can be turned around so the face is in the hall pretty easily. His other 200A panel is in the kitchen over his counter. The counter is pretty narrow so it is still easy to work in. The house was built in the late fifties, early sixties, he says it has always been like that. Would that have been code when it was installed and if so would that be something that would be "grandfathered" in? Moving the panel is not really a option, removing or relocating the counter top would not be ideal either.
 
Not sure when the work space rules went into the code, and I don't have any code books that old, but they have been in the code for a very long time.
 
The 47 book didn't have much to say about it. See pic. Screenshot_20240101_195420_Gallery.jpg
 

Attachments

  • Screenshot_20240101_195452_Gallery.jpg
    Screenshot_20240101_195452_Gallery.jpg
    695.8 KB · Views: 9
  • Screenshot_20240101_195937_Gallery.jpg
    Screenshot_20240101_195937_Gallery.jpg
    627.7 KB · Views: 9
The counter is probably pretty close to 18" but it's 240V.
In your case 240v is less than 150 volts to ground

Unsure about Code but that was common here at least into the 60s.
As far as countertops,, our inspectors are pretty lenient depending on the difficulty of relocating.
Not so much so about closets. They normally can be relocated or spun without much difficulty.
 
Thank you guys, it sounds like it probably was code when it was built, now it's just a question of whether the insurance company will grandfather it in or not.
 