Distribution panel in a commercial building.
I don't believe this is an NEC violation, but I like to put insulated bushings on the ends of all threaded fittings entering a panel or box. Also, the handle is broken off the #1 breaker. That's not the fault of the installer, but it should have been replaced when it was damaged.


- Green insulated EGC is landed on the neutral bus (the grounding bar is laying in the bottom of the panel, still in the manufacturer's packaging). Yes, I checked and it is an EGC, not a neutral with green insulation.
- Brown insulated wire is marked as a neutral conductor with masking tape.
- Two gray wires used as neutral conductors without white tape markings.
- Two open knockouts in the panel without plugs.
I don't believe this is an NEC violation, but I like to put insulated bushings on the ends of all threaded fittings entering a panel or box. Also, the handle is broken off the #1 breaker. That's not the fault of the installer, but it should have been replaced when it was damaged.