With no distinction of lightning and appliance panel now, does a panel with continuous load requires a change in its bus bar rating depending on its feeder over current protection? Thanks.
In earlier codes where there was lighting and appliance panels and power panels distinction, the power panel did not require protection of its bus bar.Per 408.36, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard. This has not changed from recent codes. The type of load doesn't change this.
In earlier codes where there was lighting and appliance panels and power panels distinction, the power panel did not require protection of its bus bar.
408.30 hasn't changed, which says that "all panelboards shall have a rating not less than the 'minimum feeder capacity' required for the load calculated in...Article 220." In my mind, this addresses the continuous load question that you are asking.