We are working in an island with 230V 60Hz supply. While the older electrical equipment came from the UK, the newer equipment has been coming from the US.
My problem is with panel ratings. When we source a 3 phase panel from the US, I ask for a 415 voltage panel and breakers. That covers the 400v 3 phase voltage.
But when I want a single phase panel, all I can get is a 240v split phase panel, which, unless i am much mistaken, is only rated 120v line to neutral and comes with two hots. People are buying these and installing them, but to me this is very wrong.
If I ask for a 415 volt rated busbar and breakers, I get a 3 phase panel.
How can I source a panel that is 230V L-N rated and single input lug?