Panel reading
mstrlucky74
NJ
How do you perform a 30-day current reading on a panel? Is it best to get a testing company involved with that? Thank you
Sent from my SM-N960U using Tapatalk
xptpcrewx
Power System Engineer
Las Vegas, Nevada, USA
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
You could do it yourself if you are qualified and know what you’re doing. If you don’t mind me asking... why do you need a 30 day reading?
MrJLH
CO
There is a requirement in the NEC (Cant reember the section) that if the load is unknown on a panel 30 day metering can be used to determine the load.
I have used these:
http://www.dranetz.com/power-quality-analyzers/
http://www.dranetz.com/product-services/current-dranetz-products/powerxplorer-px5-400/
A little pain to set up, just make sure you take into account loads such as heaters or coolers that may or may not turn on.
EC - retired
POCO Smart meters are changing things. I had a customer ask about upgrading his service for a single day of the year event. The POCO could tell me precisely when their peak usage was and the current of each phase at that time. I'm not sure if that would meet the NEC requirements but it would be something to ask the AHJ and POCO about.
ElectricMatt
Waco, tx
We do it ourselves. We actually just purchased a new DM-5 so we can do power and quality analysis. If you do not have the equipment we used intellirent(i put a link below). They have a good selection and are pretty affordable. They come with a laptop setup for your download and one day shipping.
http://www.intellirentco.com/
xptpcrewx
Section 220.87 Exception
mstrlucky74
NJ
Actually saw it on estimate document I was reviewing ....they didn't give reason ..just asked for it to be done.
Kansas Mountain
Oklahoma, United States
Lighting and Lighting Control Designs
Checking w/ POCO is definitely the way to go - free and doesn't take 30 days. . . if you're talking about a subpanel though, and not the service/MDP, then guess you're back to 30 day measuring.
ElectricMatt
Waco, tx
How much do these run ballpark?? Is the setup/wiring involved? Thanks
The one we used was about $300 for 30 days. It takes about 1-2 hours setup, this setting parameters and figuring out how to use it. I think we were charging 800 for thirty days. Remember to leave enough time for you to dig through all the data, and it is a lot!
mstrlucky74
NJ
Back on this subject but different job. Have 3 different meters on 3 different panels. Is this a " set it and forget it" type of deal to setup the meters and walk way? What about( as it says) taking meter reading every 15 minutes? Is that done automatically by setting the meter to do it? Thanks.
ElectricMatt
Waco, tx
Yes it is. Most of them can capture 30+ days of data if set at 15 minutes and you are only reading voltage and current. You can setup on on the feed for the three meters and it will record all phases simultaneously.
Depending on the equipment setup usually takes an hour. Then about another hour to remove and close up any holes. Going through the reports can be hours depending on what you’re looking for. These meters generate both graphs and table with your min/max volts and amps. It has been sufficient for any load readings that our engineers have ever wanted.
mstrlucky74
NJ
Thanks.