Yes, it could be a dedicated panel for the computers to reduce interference, or the panel could be fed by a UPS unit. If it is the latter, the owner will be real upset when you fry his UPS, and shut down all of his computers! I had a competitor who under bid me on a fire pump install on an orange box, as anyone who has worked on one of those stores knows that most of the panels are controlled by energy management, and automatically shut off at night. I knew that I would have to run the feed for the jockey pump all the way back to the electrical room about 500' away. My competitor did not, he ran it to the closest panel about 30' away which was on a contactor. About midnite the fire pump would start because the jockey pump lost power at 10:00, the sprinkler system had leaks and would loose pressure. After he figured out why it was doing it, he begrudgingly ran the feed to the electric room where he promptly installed the circuit in the computer panel which had plenty of spares. When the pump started, the 6 kva ups didn't like it a bit. Neither did the store manager.