transman2
Senior Member
- Location
- Brooklet,Ga.
I'm trying to figure what size Main I need in my 3 phase panel. It will be a 3 phase 120/208 panel with 18 spaces. My loads will be 7 booths that pull around 18 amps each and will be fed with a 2 pole breaker. So if my total connected load is 52416 VA/ 208 x 1.73 = 145.66 amps. So the main would be 150 amps. Did I do this right or do I multiply by 125%. 182 amps so 200 amp panel. Not sure. Seems like I'm missing a step!