My Esteemed Electrical Friends,
I ran across this panel schedule, and something seemed wrong to me. First off, I'm not used to seeing schedules where they just use L1 and L2. Most panel schedules I have used break up L1 & L2 into 2 columns each so you can
see the exact load being contributed at each circuit breaker.
When I look at this schedule, it seems to me that the BTS pulls 19,000 W and the surge would be pulling 0. Anyhow...
I can't figure out where the engineer got their "25% of Largest Continuous Load (LCL)" from. I tried working backwards from the total load amps, but I'm not getting figures that even make sense to me if they're rounded.
Is anybody up to the challenge on a Monday to give me some clue what's going on?
Thanks!