Just wondering how other engineers do there panel schedules. When you have a 3p-?? breaker. Do you circuit it like..

A)Panel "P1-1/3/5"
B)Panel "P1-1" and you show it on the panel schedule as a 3 pole breaker.

Are there other options?

Thanks,
Kfenn
 

tom baker

First Chief Moderator
Staff member
Re: Panel Schedule

The panel shedule would be numbered with odd and even numbers, for a 3 pole breaker in spaces 1-3-5 the panel shc would show the same description. The size can be shown in a seperate column.
 

peter d

Senior Member
Location
New England
Re: Panel Schedule

I usually think "Lights and plugs" is sufficient. Also, a few words spelled wrong is good too, like "firnace."
 

jimwalker

Senior Member
Location
TAMPA FLORIDA
Re: Panel Schedule

Would rather see lights or receptacles than have a mis labeled panel saying perhaps recepts office 307 and find out it was wrong :mad:
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: Panel Schedule

When I draw circuits on the plan view, I do list all the poles like P1,3,5. Unless it is a switchboard type panel where the spaces wouldn't be numbered.

I also draw 3 arrowheads on the home run. That way it is obvious it is a 3 pole circuit.

Steve
 

lile001

Senior Member
Location
Midwest
Re: Panel Schedule

Originally posted by steve66:
When I draw circuits on the plan view, I do list all the poles like P1,3,5. Unless it is a switchboard type panel where the spaces wouldn't be numbered.

I also draw 3 arrowheads on the home run. That way it is obvious it is a 3 pole circuit.

Steve
We quit drawing multiple arrowheads a while back. We used to have situations where several circuits were combined in one home run, such as large area open office lighting, and we would draw a half dozen arrowheads to indicate so many circuits. Now we just draw one arrowhead, label which circuits are involved ("LPC-3,5,7") and draw hash marks to indicate number of wires in the home run.

We quit drawing hash marks at every loop of wire between fitures too. I think this just caused a lot of extra work and didn't add any useful info for the electrician.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: Panel Schedule

On the Panel Schedule itself, I show the name of the load in space #1, and use ditto marks in spaces 3 and 5. If I have to refer to the source of power to a load, I describe it as ?Panel # XYZ, circuit #1, 3, 5.?

I do not use multiple arrowheads or hash marks anywhere on the power plans (not on the home runs, and not on the connections between loads).
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: Panel Schedule

I do not use multiple arrowheads or hash marks anywhere on the power plans (not on the home runs, and not on the connections between loads).
For lighting circuits, I run into a lot of 3 way and 4 way switching, double switching, and often an extra wire is required for turning on emergency fixtures if the power goes off.

But it sounds like I am wasting my time! Do you guys have any problems with the contractors not wiring things up right or not knowing how to bid a project since you don't show hash marks on the wiring runs??

Steve
 

rr

Member
Location
Georgia
Re: Panel Schedule

Originally posted by steve66:
For lighting circuits, I run into a lot of 3 way and 4 way switching, double switching, and often an extra wire is required for turning on emergency fixtures if the power goes off.

But it sounds like I am wasting my time! Do you guys have any problems with the contractors not wiring things up right or not knowing how to bid a project since you don't show hash marks on the wiring runs??

Steve
I show hash marks on power and lighting. On my Fire Alarm and Signal drawings, I have a wiring schedule with a designation. For example, on Fire Alarm drawings, a conduit that connects two horn/strobe devices might be "F2" which would be "(2)#12's in 3/4"C.".

It also helps reduce possible RFI's or change orders that might result from a contractor's mentality of "it wasn't shown on the drawing, so I didn't install it". :D

[ March 04, 2005, 01:56 PM: Message edited by: rr ]
 

marketman

Member
Re: Panel Schedule

I find hash marks to be essential. Particularly when indicating something like 3/4"c, 3#12 & #12 gnd isnt clear enough. 3#12 could be 2 hots, 1 neutral and a gnd, or it could be 3 hots and a ground. The hash marks clarify this with either 2 short and one long dash or 3 short dashes respectively. This ensures proper color coding is pulled in. When contractors are required to provide MC cable assemblies they need this info for correct purchasing.
I also add a dashed long to indicate the ground, or 2 dashed longs indicating ground and isolated ground.


PP-1/3/5 would indicate a 3 phase circuit having a hash mark containing 3 shorts and 1 long if the neutral is required.

PP-1,3,5 would indicate 3 single phase circuits when applied with a hash mark containg 3 shorts and one long, with dashed long for the ground, characteristic of a shared neutral. In this instance if 3 separate circuits were required, 3 sets of 1 short with 1 long dash would be indicated.

[ March 04, 2005, 02:33 PM: Message edited by: marketman ]
 