Hello,
I recently was tasked with creating panel schedules for large custom equipment that have panel boxes installed into them and are then shipped and field wired to a feeder by a onsite electrician.
On these schedules if I have a piece of equipment that is 208v 2080VA they will divide the VA between A and B phase. So they would enter 1040 on A phase and 1040 on B phase. Then they will at the bottom of the form add the 2 phases back together to get a total VA for the schedule of 2080VA.
Now when i look at that i see 1040VA on each phase and instantly think it's a 5A load and that a 10A breaker would be needed. However, I'm being told i'm incorrect.
In all my years as a electrical engineer I have never heard of dividing the VA of a piece of equipment between the 2 phases. The 2 phases share the load equally. So there would in fact be 10A on each phase. Which is 2080VA on phase A and B alike. I would never add the VA from phase A to Phase B to get a total VA for the panel. It just doesn't make sense to me.
This has become a heated debate here and as I am not an Electrician I'm a little unsure of what is really correct. I just posed the question.
So my question is what is the correct way to do this and why/how is it the correct way?
Thanks,
Kyle
I recently was tasked with creating panel schedules for large custom equipment that have panel boxes installed into them and are then shipped and field wired to a feeder by a onsite electrician.
On these schedules if I have a piece of equipment that is 208v 2080VA they will divide the VA between A and B phase. So they would enter 1040 on A phase and 1040 on B phase. Then they will at the bottom of the form add the 2 phases back together to get a total VA for the schedule of 2080VA.
Now when i look at that i see 1040VA on each phase and instantly think it's a 5A load and that a 10A breaker would be needed. However, I'm being told i'm incorrect.
In all my years as a electrical engineer I have never heard of dividing the VA of a piece of equipment between the 2 phases. The 2 phases share the load equally. So there would in fact be 10A on each phase. Which is 2080VA on phase A and B alike. I would never add the VA from phase A to Phase B to get a total VA for the panel. It just doesn't make sense to me.
This has become a heated debate here and as I am not an Electrician I'm a little unsure of what is really correct. I just posed the question.
So my question is what is the correct way to do this and why/how is it the correct way?
Thanks,
Kyle