Is there a requirement that elevators need to be fed from a separate panel with other load? Thanks!
benaround
Arizona
anbm, I don't understand ' seperate panel with other load ' , but, normally the elevator
pump and control panel is a feeder by itself and the other circuits related to the elevator
are not on this feeder.
anbm
I mean elevator motors can't share same panel with lighting, other hvac, heating, motor load etc.
chris kennedy
Miami Fla.
Typical they are fed from the buildings MDP with shunt trip breakers connected to the fire alarm system. There are no requirements in 620 as to where the normal power comes from.
nakulak
I don't think there are nec requirements for this, but I believe that there may be ANSI requirements (and possibly articles from other nfpa documents ?)
quogueelectric
new york