The spec of 20 space/40 circuit as compared to 20 space/20 circuit panel kind of confuses me.
Both are physically the same size. Does the 40 circuit (versus 20 circuit) allow a full panel of “twins”?
is the buss heavier to allow for more circuits?
They are both rated for 100 amps. What’s the difference?
A very basic question that has confused me for a while.
 
Does the 40 circuit (versus 20 circuit) allow a full panel of “twins”?
Yes.

is the buss heavier to allow for more circuits?
No. The total current would be the same as a 40 sp/40 ckt panel.

They are both rated for 100 amps. What’s the difference?
The bus is designed to accept tandems.
 
Yes.

No. The total current would be the same as a 40 sp/40 ckt panel.

The bus is designed to accept tandems.

But 40 only if no AFCI or GFCI breakers, no tandem for those yet, that I've seen. Siemens claims to have one but haven't seen it.
 
I just installed a BR 30/60 panel yesterday and it did not have notches in the fuss. It was 100% exactly like the supposed non CTL panel.

I was completely surprised, and very thankful I have a whole box full of non CTL twins, both 15 and 20

I haven't taken pictures of it because I'm not finished working in it, but when I go back on Tuesday I'll have some.

Having typed that, now watch me get back Tuesday and it'll be a case where somebody swapped out that panel in the box 🙄

😅😅😅
 
Depending on how grounds are dealt with, a 20/20 panel will have about 20 neutral bus positions. A 20/40 ought to have close to 40. I have a 30/40 main service panel and it is short on neutral lug space. If I could untangle all the grounds I could triple up some of them. But I'm just going to rip it out and do it all over. New panel will be 32/64 with hardly any twins because most things need AFCI now (will have a separate panel for all the double poles and a few more circuits since I actually need 40 to 50 slots). Should never have a neutral lug issue in that panel or the new main one again.
 
Depending on how grounds are dealt with, a 20/20 panel will have about 20 neutral bus positions. A 20/40 ought to have close to 40. I have a 30/40 main service panel and it is short on neutral lug space. If I could untangle all the grounds I could triple up some of them. But I'm just going to rip it out and do it all over. New panel will be 32/64 with hardly any twins because most things need AFCI now (will have a separate panel for all the double poles and a few more circuits since I actually need 40 to 50 slots). Should never have a neutral lug issue in that panel or the new main one again.
I have never understood why they make a panel that's supposedly good for 30 circuits, and I get 16-20 spaces in the neutral bar. 40 circuit panel and you get about 28 neutral bar spaces
🙄

But I guess that's getting better with the plug on neutral breakers.
 
I have never understood why they make a panel that's supposedly good for 30 circuits, and I get 16-20 spaces in the neutral bar. 40 circuit panel and you get about 28 neutral bar spaces
🙄

But I guess that's getting better with the plug on neutral breakers.
Because there was a day when competent electricians knew how to wire circuits using MWBC and were not afraid to.
 