My question relates to this panel, is there anything code or listing wise prohibiting using the main lugs of a panel where a backfed main has been installed, to subfeed another panel?

IMG_0209.jpg


Since the breaker is bolt-on, any concerns about a retainer/ hold down bracket do not apply. Please forgive my cell phone pic & the pic will not display w/ the correct rotation.

From the 2011 NEC, 408.36(D). (F) in earlier editions.

(D) Back-Fed Devices. Plug-in-type overcurrent protection
devices or plug-in type main lug assemblies that are
backfed and used to terminate field-installed ungrounded
supply conductors shall be secured in place by an additional
fastener that requires other than a pull to release the
device from the mounting means on the panel.
 
My question relates to this panel, is there anything code or listing wise prohibiting using the main lugs of a panel where a backfed main has been installed, to subfeed another panel?

Only the calculated load is a consideration. You can feed as many panels as you want from the back fed panel, through the lugs, as long as 215.2 and 408.30 are met.
 