Panel to Panel

jimbo172005

New User
Location
Reno, Nevada
Occupation
Journeyman Wireman
1st Floor 400 amp rated panel feeding into the 2nd floor 400 amp panel is this right? Or do i need to upsize my 1st floor panel to 800,also the Circuit breaker on 1st floor panel is not rated for two wires…..in each phase terminal lug.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The 400 amp 1 st floor may be adequate but you'll need to do a load calculation to ensure that it is. The two lugs per terminal may require you to change the terminals to ones listed for more than one conductor.

Welcome to the Forum. :)
 
Top