Karl H
Senior Member
- Location
- San Diego,CA
On a 208 3 phase panel should the tag read 208/120 or 120/208?
480 3 phase- 480/277 or 277/480?
480 3 phase- 480/277 or 277/480?
The preferred ANSI method is:
120/240 single phase
208Y/120 three phase
240/120 three phase
480Y/277 three phase
Supply systems are listed at the nominal voltages listed in the NEC, 120, 208, 240, 480, and 600V.
Motors are listed at utilization voltages of 115, 200, 230, 460, and 575V.
Connecting types of devices like lamp holders and fuse holders are listed at a maximum voltage of 125, 250 and 600V.
Plugs and receptacles are listed based on their specific configuration.
It seems that appliances may be listed at no specific voltage method.
Now, just to be picky. The ANSI/IEEE convention for naming system voltages is:
Multi-wire grounded (bonded) single phase - list the L-G voltage first, then a forward slash and then the L-L voltage: 120/240 or in this case 104/208.
Multi-wire grounded (bonded) three phase - list the L-L voltage first, then the letter Y if applicable, then a forward slash, and finally the L-G voltage: 208Y/120, 480Y/277, and 240/120.
I have spent 30yrs trying to unlearn the bad habit of saying 120/208V. Now I try (but often fail) to include the number of phases and wires, as I find it does reduce confusion, for example: 120/240V 1PH3W and 240/120 3PH 4W