Panel vs breaker rating

Status
Not open for further replies.
Location
New Mexico
Occupation
Contractor
I am looking to install a load center that is 200 amps the bus is rated at 22kA, the breaker is an I-line breaker 200 amps 2 pole rated at 14kA. Does the panel having a higher rating get affected by the breaker not being the same rating?
 
This site is designed for:
  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
This NEC® Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

Knowledge and the practical application of the National Electrical Code is an essential part of all electrical installations. If it's important for you to understand the National Electrical Code, then look no further.

To better help us serve you, please be sure to update your account details with your occupation field and location if you have not done so already. You can access your account details by clicking on your account name at the top right of the page when on the forums.
 
But… no. The “rating” (bracing) of the panel has no affect on the interrupt rating of the breakers, they are totally different things. But it would need to be equal to or greater than the breaker rating. Your electrician would understand this.
 