Can I set a panel with MLO with a set of 3/0 conductors (tap from a gutter with 2 sets of 250 KM) after a 600 Amp main disconnect switch.
Can I set a panel with MLO with a set of 3/0 conductors (tap from a gutter with 2 sets of 250 KM) after a 600 Amp main disconnect switch.
But that does not address the first question that Chris asked in post #3.Quickest, easiest way is with a main breaker in the panel
But that does not address the first question that Chris asked in post #3.
There are two separate issues here. The first is how to connect the tap conductors. The second is how to protect the tap conductors and the panel itself.
No. But the OP did describe an illegal way to do it. That was my point. I was not talking about the manner of making the connections. I was echoing Chris' comment about tapping a single conductor per phase into a feeder that has two conductors per phase.The OP did not ask how to make the tap connection at all Charlie.