E EC70 New member Location TAMPA,FL Jul 4, 2012 #1 In healthcare, you have to bond all the panels that serve a patient care area together. If I run this bond in conduit, do I have to put a meg bushing on or is the locknut considered to be serving the same purpose (steel set screw connector)?
In healthcare, you have to bond all the panels that serve a patient care area together. If I run this bond in conduit, do I have to put a meg bushing on or is the locknut considered to be serving the same purpose (steel set screw connector)?
roger Moderator Staff member Location Fl Occupation Retired Electrician Jul 4, 2012 #2 A locknut is all that is required. Roger