All,
Scope of project - adding (3) new HVAC units, totaling in 190A FLA.
Existing electrical - 800A, 120/208V main switchboard with (1) space.
I am planning on adding (1) new breaker to the existing SWBD to feed (1) new panel.
I am trying to size the breaker feeding the panel.
Should the breaker serving the panel be 250A? (per 210.20(A)), which would give 125%x190A = 237.5A minimum)
Or since I am sizing each breaker on the panelboard with at least 125% (in my case 175% for a c/b) , I can use a 225A breaker to feed the panel since there is only 190A of load?
I think I am thinking too much on this and starting to go back and forth...
Any help appreciated! Thanks
Scope of project - adding (3) new HVAC units, totaling in 190A FLA.
Existing electrical - 800A, 120/208V main switchboard with (1) space.
I am planning on adding (1) new breaker to the existing SWBD to feed (1) new panel.
I am trying to size the breaker feeding the panel.
Should the breaker serving the panel be 250A? (per 210.20(A)), which would give 125%x190A = 237.5A minimum)
Or since I am sizing each breaker on the panelboard with at least 125% (in my case 175% for a c/b) , I can use a 225A breaker to feed the panel since there is only 190A of load?
I think I am thinking too much on this and starting to go back and forth...
Any help appreciated! Thanks