One may be able to use products like those you mentioned or modify the wall in some way to preserve the finish rating, but you can't just cut into the finish rating with that large of a penetration. Any method used may be good idea to pre approve with the inspector as well or you may be doing it over and repairing what you damaged on the original finish.3m has an endothermic mat for this type of installation.
http://solutions.3m.com/wps/portal/...hermic-Mat-E-5A-4?N=5433099+3294069023&rt=rud
http://www.google.com/url?url=http:...ic+mat&usg=AFQjCNHOYcA186aZ0G3Qh5OZJvVlFWEyGw
Just make sure you get an engineering judgement or have a listed penetration detail available for the inspector.
Problem is there is no proper way to do it that is "approved" People try to do it all the time and as was kind of mentioned, it's gets messed up and then you've really created an issue.Thanks for the input. The panel is going to be put in a new corridor wall. The takeaway is that it can be done, just with the proper materials to maintain the rating?
Problem is there is no proper way to do it that is "approved" People try to do it all the time and as was kind of mentioned, it's gets messed up and then you've really created an issue.
Remember that a two hour wall is two layers of drywall, a two by four, and two layers of drywall. The vertical seams of the drywall are not allowed to over lap either. So how would you build an approved wall cavity with those issues in mind?
That's my point about no approved method. In most two hour assemblies you have to flag the drywall through.How do you not overlap vertical seems in a corner?
Does the two by four need to be in there or is the net four layers of drywall the most critical thing?
I have seen instances where they allowed four straight layers with nothing else in between to plug an old window or other existing opening where they wanted a two hour rating.
Yes, ...the 2 x 4's are part of the fire tested assembly; as well as, the 4 layers of"Does the two by four need to be in there or is the net four layers of drywall the most critical thing?"
Thanks for the input. The panel is going to be put in a new corridor wall. The takeaway is that it can be done, just with the proper materials to maintain the rating?
That's my point about no approved method. In most two hour assemblies you have to flag the drywall through.
If you look in the Gypsum manual or any of the fire protection product manuals, you will not find anything that would allow you to install a panel in any rated wall, let alone a two hour one. "Approved" means just that. "Allowed" is another thing.Im not sure if by "no approved method" that includes 5-siding the panel within the stud bay?