jumper Senior Member Location 3 Hr 2 Min from Winged Horses Sep 10, 2010 #2 No, not if it is a dwelling. 240.24 (E) Not Located in Bathrooms. In dwelling units and guest rooms or guest suites of hotels and motels, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms Last edited: Sep 10, 2010
No, not if it is a dwelling. 240.24 (E) Not Located in Bathrooms. In dwelling units and guest rooms or guest suites of hotels and motels, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms
J jbolen Senior Member Sep 10, 2010 #3 code section code section I agree having problem finding code section to back it up.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Sep 10, 2010 #4 jbolen said: I agree having problem finding code section to back it up. Click to expand... I added the code section into post 2#.
jbolen said: I agree having problem finding code section to back it up. Click to expand... I added the code section into post 2#.