rroark0003
Can a three panel with a main be use on a single phase service?
Does it matter which two of the three lugs on the three phase breaker are used? Also, is there a NEC reference?
Yes, but this would not apply to a single phase SERVICE...The NEC is silent on the subject, except in the general rule that the instructions of the panelboard maker must be followed.
If the manufacturer says not to use it for three wire single phase, then you would be out of luck.
The only preference that I see is the convention that in a high leg delta the "different" leg, the high leg, must be landed on the B phase line.
By leaving the B phase unconnected you are in parallel with that same idea, even though it is not a requirement.