SPARKLEY
Member
- Location
- Denver, CO
- Occupation
- Electrician
408.3(A)(2) Service Panelboards, Switchboards, and Switchgear. Barriers shall be placed in all service panelboards, switchboards, and switchgear such that no uninsulated, ungrounded service busbar or service terminal is exposed to inadvertent contact by persons or maintenance equipment while servicing load terminations.
I find this barrier requirement wording too vague, and I don’t find any help in reading UL67 5.4.2.
For example, assume a MLO loadcenter (and that the exception of 408.36 does not apply):
1. Does “service terminal” include main lugs?
(2. Even with barriers on the main lugs, how would barriers on busbars sections be accomplished, i.e., exposed busbars with no breakers on them?)
3. Some manufacturers must also be confused because they do not include barriers with MLO loadcenters. Not to mention any names, but see the label below which conspicuously omits MLOs when ordering barrier kits…

Can anyone shed light on MLO barriers? Thank you in advance
I find this barrier requirement wording too vague, and I don’t find any help in reading UL67 5.4.2.
For example, assume a MLO loadcenter (and that the exception of 408.36 does not apply):
1. Does “service terminal” include main lugs?
(2. Even with barriers on the main lugs, how would barriers on busbars sections be accomplished, i.e., exposed busbars with no breakers on them?)
3. Some manufacturers must also be confused because they do not include barriers with MLO loadcenters. Not to mention any names, but see the label below which conspicuously omits MLOs when ordering barrier kits…

Can anyone shed light on MLO barriers? Thank you in advance