panelboard neutral

Status
Not open for further replies.

stephen krone

New member
Is it required to connect a neutral on a 240/120 ("single phase") rated panel that is connected to a 208Y/120 three phase system when the panel feeds only 208 volt loads?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Re: panelboard neutral

No. There is never a requirement to install unused conductors.

However, why don't you want to?
Meeting minimum requirements rarely provides an optimum design.
 

charlie

Senior Member
Location
Indianapolis
Re: panelboard neutral

Originally posted by Stephen Krone:
Is it required to connect a neutral on a 240/120 ("single phase") rated panel that is connected to a 208Y/120 three phase system when the panel feeds only 208 volt loads?
Yes, if the panelboard you are talking about is service equipment and being fed from a 208Y/120 volt transformer. See 250.24(B) which states "Where an ac system operating at less than 1000 volts is grounded at any point, the grounded conductor(s) shall be run to each service disconnecting means and shall be bonded to each disconnecting means enclosure."

In all likelihood, this is a distribution panelboard and my answer doesn't apply. If that is the case, see Jim's answer and pay special attention to his comments following his answer. :cool:
 