I recieved the following email and I hope the orginator will come here for all the answers:
Hello Tom;
My name is Hector and I'm from Laredo,Tx
I am a Master Electrician and I have a bachelor's degree in Electrical engineering from Mexico since 1980.
My question is....Is it prohibited to use Load Centers in commercial sites instead of panelboards?
I have installed a 600 Amps Service Entrance (Main) in 480/277 volts;Next to main disconnect, we have a busduct to connect 8 new services for commercial suites (future loads).Then, next to busduct we have installed a meter house with a panelboard (bolt on breakers).That panelboard feed a 45 Kva transformer to low voltage from 480/277 to 208/120 volts and next to transformer we installed a 125 amps Load Center (snap in breakers) for 120 volts lighting loads only.
I looked for any Info in the CODE book but I did not find anything referent to this.The Electrical local inspectors tell me that I need to replace the load center for a panelboard because the electrical CODE does not permit load centers on commercial buildings like in this case.They said only panelboards are permitted. Also, the sub panels to be installed in a future inside of the building (suites) will be panelboards. Is this ordinance correct by the local inspectors? And what makes the diference between them? (apart from costs),when can I use panelboards and when can I use Load Centers?.
Note: My question is for lighting and duplex receptacle loads only, with a feeder breaker box not bigger than 200 amps in commercial centers, three or single phase: Not Accu's or Ahu's or motors loads included on these questions.
I appreciate your comments to my questions.
Hello Tom;
My name is Hector and I'm from Laredo,Tx
I am a Master Electrician and I have a bachelor's degree in Electrical engineering from Mexico since 1980.
My question is....Is it prohibited to use Load Centers in commercial sites instead of panelboards?
I have installed a 600 Amps Service Entrance (Main) in 480/277 volts;Next to main disconnect, we have a busduct to connect 8 new services for commercial suites (future loads).Then, next to busduct we have installed a meter house with a panelboard (bolt on breakers).That panelboard feed a 45 Kva transformer to low voltage from 480/277 to 208/120 volts and next to transformer we installed a 125 amps Load Center (snap in breakers) for 120 volts lighting loads only.
I looked for any Info in the CODE book but I did not find anything referent to this.The Electrical local inspectors tell me that I need to replace the load center for a panelboard because the electrical CODE does not permit load centers on commercial buildings like in this case.They said only panelboards are permitted. Also, the sub panels to be installed in a future inside of the building (suites) will be panelboards. Is this ordinance correct by the local inspectors? And what makes the diference between them? (apart from costs),when can I use panelboards and when can I use Load Centers?.
Note: My question is for lighting and duplex receptacle loads only, with a feeder breaker box not bigger than 200 amps in commercial centers, three or single phase: Not Accu's or Ahu's or motors loads included on these questions.
I appreciate your comments to my questions.