Panelboard or switchboard

Status
Not open for further replies.

codequestion

Banned
Location
MD, USA
Is there anywhere in NEC 2014 it says panelboard or switchboard shall not be overloaded and that demand and connected load calculation is required?

Sent from my SM-G935U using Tapatalk
 
If I recall correctly you had mentioned your supervisors are Mechanical Engineers.
Is this correct?
Can I ask if your finished plans are being sealed (stamped) by a Mechanical Engineer ?
 
Is there anywhere in NEC 2014 it says panelboard or switchboard shall not be overloaded and that demand and connected load calculation is required?

Sent from my SM-G935U using Tapatalk

There is always 110.3.....don't know for sure offhand, but I assume 408 has language about sizing to serve the load. One interesting thing to note is panelboards require protection at their rating (408.36) but switchboards do not.
 