Defenestrator
Member
- Location
- Denver, CO
- Occupation
- Electrical Engineer
How do you guys place panelboards around a facility to ensure adequate coverage?
Are there any rules of thumb used to place panelboards? What do power factor do you use for voltage drop calcs, 0.85? What percentage of max load for a circuit would you use to calculate the voltage drop? 80% of the derated continuous load? do you always assume the smallest allowable conductor according to the ampacity tables in section 310.15 of the NEC?
Some people draw a circle with a certain radius with the panelboard centered on the equipment, but to me that seems kinda lazy because circuits don't travel in a straight line, they run orthogonal to the lines of the building. Others place a panelboard centrally for a certain amount of square footage, but im not sure where they get those numbers
my situation is that i need to place 120/208v and 277/480v panelboards but the circuits have to go up 25ft and then back down 25ft. Its new construction, not renovation, so i have some leeway with where i want to place the panelboards. The engineer I'm working with told me to draw a diamond, whose size is determined my the max circuit length based on vdrop, minus vertical offset
i know im overthinking this and there must be some easier way to do it. Any advice would be appreciated
Are there any rules of thumb used to place panelboards? What do power factor do you use for voltage drop calcs, 0.85? What percentage of max load for a circuit would you use to calculate the voltage drop? 80% of the derated continuous load? do you always assume the smallest allowable conductor according to the ampacity tables in section 310.15 of the NEC?
Some people draw a circle with a certain radius with the panelboard centered on the equipment, but to me that seems kinda lazy because circuits don't travel in a straight line, they run orthogonal to the lines of the building. Others place a panelboard centrally for a certain amount of square footage, but im not sure where they get those numbers
my situation is that i need to place 120/208v and 277/480v panelboards but the circuits have to go up 25ft and then back down 25ft. Its new construction, not renovation, so i have some leeway with where i want to place the panelboards. The engineer I'm working with told me to draw a diamond, whose size is determined my the max circuit length based on vdrop, minus vertical offset
i know im overthinking this and there must be some easier way to do it. Any advice would be appreciated