I work for a consulting engineering firm as an electrical engineer. We have a difference of opinion in our office on sizing for a panelboard or switchboard serving mechanical loads.
Let's say the FLA of a dozen or more mechanical units (where the largest load is taken at 125% FLA) sums to 1250Amps, 3-phase, at 480Volts.
In the past, I typically have applied a reasonable demand factor to the load of, maybe 75-80%. 1250A * 80% = 1000A. Therefore a 1200A panel is acceptable.
My colleague believes the NEC does not allow us to take such demands because they are not code-driven and, so, one would need to provide at least a 1600A switchboard to serve the load.
Are either of us correct? Or is he simply being more conservative and I am being more aggressive in our design approaches? I feel like if we were to follow his approach for some jobs, equipment would be insanely oversized.