I have an installation by a computer/telephone supplier where a UPS supplies a 30A two pole panelboad.

The UPS is supplied by a 208V single phase circuit. The UPS then feeds a 5 kVA autotransformer (buck/boost) which then supplies the panelboard. The panelboard supplies six 20 A single pole circuit breakers to feed receptacles to supply power to various computer equipment.

Is a UPS considered a separately derived system? If so, how is to be grounded/bonded?

The issue I have is the paneboard has only one terminal bar in it and both the neutrals and equipment grounding conductors are all interconnected.

I think this is a violation of the NEC and the neutrals and grounds should be on separate terminal bars like a subpanel.

The vendor says this is how they install all of their panels fed from a UPS.

Is having the neturals and grounds interconnected at the panel acceptable? If not what is the NEC reference - is it 250.24 (A) (5)?
 
In many cases the output of a UPS is SDS and the netural to bond ground is on the load side of the UPS. In that case you can put the neutrals and grounding conductors on the same terminal as long as the sytem bonding jumper is in that panel. I don't understand how or why you use an autotransformer on the UPS.
Don
 
I don't know why the vendor used an autotransformer either and they have not supplied drawings of their system.

If the UPS is a separtely derived system, how can I check that is grounded/bonded properly? Or all of those connections internal to the UPS?
 