Panelboard supplied through transformer- OCPD.

Status
Not open for further replies.

housemoney

Member
Location
Midwest
Occupation
Engr
Would appreciate a quick simple sanity check here: I have a 3 phase MLO 208/120 30 circuit panelboard fed from a 3 phase transformer as shown below.

Per NEC 408.36 (B) this panelboard requires secondary side overcurrent protection-MCB, fusible disconnect etc.. (not MLO straight off the transformer)?

The exception: 240.21 C/1 would not apply
 

Attachments

  • Capture.JPG
    Capture.JPG
    14.1 KB · Views: 38

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Many decades ago this was a common installation method. Changes to the NEC made it non-compliant for new installations.

But, many designers continue to do what they have always done.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree, the installation that is depicted is not code compliant.