Been perusing the forums, and haven't found the answer to this one yet:
We're looking at putting in a 2500 kVA 12470-480V transformer to feed a 3000A MLO panel with 5 or 6 large molded case breakers. It hasn't been determined whether it will be a Delta-Delta or Delta-Wye transformer yet.
This is in a very large industrial plant, and is a very small piece of their electrical system.
The cable length between the transformer secondary and the panel is roughly 65 feet.
We're planning to install CTs on the transformer secondary and use a protective relay on the primary side of the transformer to trip the primary side breaker for secondary side faults.
Does this satisfy NEC requirements for panelboard overcurrent protection (408.36) and for transformer secondary conductor overcurrent protection (240.21(C))?
Thanks!