E estimator41 New member Jun 17, 2005 #1 I am having a problem with an AHJ telling me that we have to relocate a panelboard that is installed in a bathroom at a Walmart, as i understand the NEC it applies only to dwelling unit bathrooms. Anybody have a differnt view?
I am having a problem with an AHJ telling me that we have to relocate a panelboard that is installed in a bathroom at a Walmart, as i understand the NEC it applies only to dwelling unit bathrooms. Anybody have a differnt view?
rcarroll Senior Member Location Fort Collins, Colorado Jun 17, 2005 #2 Re: Panelboards in bathrooms-commercial 240.24(E)is clear. As long as you have working clearances, you should be ok. Ask the AHJ for a code reference.
Re: Panelboards in bathrooms-commercial 240.24(E)is clear. As long as you have working clearances, you should be ok. Ask the AHJ for a code reference.