1-199 Log #159 NEC-P01
(110-26(A))
Final Action: Reject
Submitter: W. Creighton Schwan Hayward, CA
Recommendation:
Add to (A), starting in line 7:
The grade, floor or platform of the working space shall be horizontal, flat, and level, except where necessarily sloped to drain, and
smooth without projection or indentation.
Substantiation:
This change will provide a specific requirement to correct these conditions observed in the field:
1. Panel boards and toggle switches in stairway walls.
2. Outdoor disconnects where the grade slopes away at such an angle or is so rocky that the working space is there, but safe footing is
not possible. This is a safety issue. Working is unsafe where the footing is not level.
Panel Meeting Action: Reject
Panel Statement:
The proposed requirement is too restrictive. The submitter notes that it would preclude a toggle switch in a stairway wall. There is no
justification for such a broad restriction. Qualified persons routinely work safely from ladders or scaffolding that may be required in the
workspace.
Number Eligible to Vote: 12
Affirmative: 12