Panelboards on hallways

Status
Not open for further replies.
No, the NEC doesn't as long as the required working space clearance is maintained.

The building codes might have restrictions though.

Chris
 
I agree with Chris. Let me add that you need to coordinate with the Architect, to make sure the walls are thick enough to accomodate a flush mounted panel.
 
alberbon said:
Does the code mention any limitation to place panelboards on hallways??

thanks

I'm assuming your Q relates to a 1-family dwelling, and if so, I would say "no". If the panelboard is proposed to be mounted within the wall of a legally required exitway in some other type of occupancy that requires a fire-resistance rating, then the answer would be "not permitted by building code." Depends on your area. Always consult with the AHJ. :)
 