I am designing a boiler room panel that is rated 200A and am planning on running a 25hp motor, 3hp motor 1/2hp and a 1/3hp. Does anybody have an objection to running all these motors from a 200A panel? The currents from these motors when u factor in the three phases, comes to 96A. So I am feeding the panel with a 150A circuit breaker from a main distribution panel. And the 200A is a main lug only.
Another question, do i require disconnect switches for these motors if the boiler room panel is in sight of the motors? In other words, does a circuit breaker in a panel qualify as a disconnecting means?
SIDE NOTE: These motors are part of a boiler system, where there is also a boiler control panel, and it seems that the boiler controls the motors by Thermal Switches, but I am pretty sure, that the boiler room panel will carry the loads for the motors, while the boiler control panel, dosn't see these loads, it just sends a signal to the switches to open/close as the configuration requires. Thanx.
[ July 24, 2003, 09:14 AM: Message edited by: bonding jumper ]
Another question, do i require disconnect switches for these motors if the boiler room panel is in sight of the motors? In other words, does a circuit breaker in a panel qualify as a disconnecting means?
SIDE NOTE: These motors are part of a boiler system, where there is also a boiler control panel, and it seems that the boiler controls the motors by Thermal Switches, but I am pretty sure, that the boiler room panel will carry the loads for the motors, while the boiler control panel, dosn't see these loads, it just sends a signal to the switches to open/close as the configuration requires. Thanx.