Panels on adjacent walls

Status
Not open for further replies.

sixt9ss

New member
If two 20" panelboards are installed on adjacent walls(in a corner),can they be butted together and still maintain the 30" working clearance? Is there a minimum side clearance?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Panels on adjacent walls

Yes you can do this, the 30" clearance does not have to be centered on each panel, this no different from filling one wall with panels right next to each other.

If you are surface mounting the panels make sure you leave a space from the corner equal to the depth of the panel with covers installed.

The edge of one panel can not go in front of the other one.
 
Status
Not open for further replies.
Top