Is is possible to estimate approximately the size of paralalling needed for a 2.5MW genset with only having the genset size? THanks.
Do you mean physical size, i.e. dimensions, or size as in rating?
More info would be helpful.
That's pushing it for 4,000A gear, need 5,000A.
2.5 MVA/.85 pf = 2941 kVA.
FLA would be 3538A. +15% would be 4,068A at 480V.