Re: parallel 1/0 conductors in PVC
The cable will produce heat just because of resistance loss But
don
additional heat in your proposed installation do to the inductive reactance caused by separating the phase groupings.
inductive reactance heating should not happen if the phase is run in plastic as sokkerdude said
sokkerdude
PVC conduit, that does not pass through any metal.
But I don't see where the code allows for the instlation of the same phase in the same conduit other than underground?
I have always have thought that they must be installed so that all conductors of a circuit are in each raceway?
Look at 300.3 (B) (1)
(1) Paralleled Installations. Conductors shall be permitted to be run in parallel in accordance with the provisions of 310.4.
The requirement to run all circuit conductors within the same raceway , auxiliary gutter, cable tray, trench, cable, or cord shall apply separately to each portion of the paralleled installation, and the equipment grounding conductors shall comply with the provisions of 250.122. Parallel runs in cable tray shall comply with the provisions of 392.8(D).
Exception:
Conductors installed in nonmetallic raceways run underground shall be permitted to be arranged as isolated phase installations. The raceways shall be installed in close proximity, and the conductors shall comply with the provisions of 300.20(B).