Hi
My question is related to the derating rules applied to 90 degC cables.
When I am using a 90 degC cable in 40 degC ambient temp, I will apply correction factor 0,91 and check if this complies with 75degC conductor of same size.
Example:
Amb = 40 degC
Non-continous current = 100 A
90degC conductor - 3AWG : 115A x 0,91 = 104,65A
Check with 75 degC conductor 3AWG: 100A ampacity = OK to use 90degC 3AWG conductor.
For parallel scenario is:
6 current carrying conductors in conduit = 0,8 adjustment factor
30 degC amb = 1 correction factor
Non-continous current: 650A
2 x 500kcmil 90 degC conductors are chosen.
Total ampacity = 430*2*0,8 = 688A
Check with 75degC conductor: 380 x 2 = 760A --> OK
My question is, should I do the 75degC check as above or should I also add adjustment factors to the check as below?
380 x 2 x 0,8 = 608A --> NO OK.
Hope that my question makes sense to you.
Thanks in advance
My question is related to the derating rules applied to 90 degC cables.
When I am using a 90 degC cable in 40 degC ambient temp, I will apply correction factor 0,91 and check if this complies with 75degC conductor of same size.
Example:
Amb = 40 degC
Non-continous current = 100 A
90degC conductor - 3AWG : 115A x 0,91 = 104,65A
Check with 75 degC conductor 3AWG: 100A ampacity = OK to use 90degC 3AWG conductor.
For parallel scenario is:
6 current carrying conductors in conduit = 0,8 adjustment factor
30 degC amb = 1 correction factor
Non-continous current: 650A
2 x 500kcmil 90 degC conductors are chosen.
Total ampacity = 430*2*0,8 = 688A
Check with 75degC conductor: 380 x 2 = 760A --> OK
My question is, should I do the 75degC check as above or should I also add adjustment factors to the check as below?
380 x 2 x 0,8 = 608A --> NO OK.
Hope that my question makes sense to you.
Thanks in advance