MWh_Pro
- Lakewood, CO
I've just gotten done reading an article from NREL on arc fault detection and mitigation for PV, and I've been thinking: what's a practical strategy for reducing parallel arc faults?
For your reference, here's the article to which I am referring: "Low Cost Arc Fault Detection and Protection for PV Systems" by Scott McCalmont / Tigo
The article mentions that a major difference between series arc faults and parallel arc faults is that the former is driven by the connected load (e.g. inverter), whereas the latter is driven by the source (PV modules). This makes extinguishing parallel arc faults inherently difficult, because removing the load will actually provide more energy to the fault. Proposed solutions include safely shorting the PV source to ground (difficult), or module level electronics that disconnect the PV source at the junction box or before the string wiring (probably less difficult). One major connection that Scott makes is that parallel arc faults can be the end result of undetected ground faults. In that sense the best defense is a good offense, and that in lieu of a Type 2 (parallel) AFD/AFCI, it is likely that most parallel arc faults could be prevented by more sensitive ground fault protection. What are your thoughts on this? Do you see a distinct advantage in preventing parallel arc faults using "floating"/ungrounded PV arrays over the more common grounded ones (due to the greater sensitivity of GFI's in such inverters)?
Until there are listed parallel AFD devices, what do you think is an acceptable plan for parallel arc fault protection? Below are some ideas:
- Module level optimizer with Type 1 AFCI built in. Any combiner boxes are basic and without detection hardware. The noise spectra for Type 1 and Type 2 faults is essentially identical, so this probably provides adequate protection for both types.
- String inverter with Type 1 AFCI and standard GFCI included
- Type 1 AFCI enabled combiner boxes and standard GFCI @ inverter
- Type 1 AFCI combiner box w/ built in GFCI
I know there's a lot here, and I appreciate any input you may have. I've been studying this stuff a bit and there aren't many people who I know personally who are well-versed on the subject. I figured I'd try my luck at the Mike Holt Forum, as the quality of responses tends to be quite good =)
Thanks in advance,
Dave
Thanks in advance,
Dave